配电房(室)在什么情况下必须上气体灭火系统呢

配电房(室),或者信息机房,在什么情况下必须上气体灭火系统呢

平苹萍 | 2023-08-17 17:10
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

同同不同 2023-08-18 07:31 10 [回复]举报

按建规要求应该是依据重要性,有点模糊

张治福 2023-08-31 11:56 00 [回复]举报

建规上的很含糊,基本上是根据经济性和重要性自行决定,技术方面,主要是项目的设计人员决定。

黄辉 2024-01-11 16:49 00 [回复]举报

按《建规》8.3.8条条文说明判断。
(2) 特殊重要设备,主要指设置在重要部位和场所中,发生火灾后将严重影响生产和生活的关键设备。如化工厂中的中央控制室和单台容量300MW机组及以上容量的发电厂的电子设备间、控制室、计算机房及继电器室等。高层民用建筑内火灾危险性大,发生火灾后对生产、生活产生严重影响的配电室等,也属于特殊重要设备室。

是否重要,这个可由业主和设计院判断。

潘天坤 2024-07-01 00:21 00 [回复]举报

一般认为附属在高层民用建筑内(非独立建造的)的配电室属于特殊重要设备室,应设置自动灭火系统,并宜采用气体灭火系统  

其他建筑的配电室可以参照执行,不做强制要求,不过有时候设计单位认为一些区域比较重要也会设置自动灭火系统  

从建规GB50016来说,A、B级电子信息系统机房内的主机房应设置自动灭火系统,并宜采用气体灭火系统,其他级别未做要求

不过按照数据中心设计规范 GB50174-2017要求,C级数据中心的主机房宜设置气体灭火系统,也可设置细水雾灭火系统或自动喷水灭火系统;总控中心等长期有人工作的区域应设置自动喷水灭火系统

建规GB50016条文说明提及:高层民用建筑内火灾危险性大,发生火灾后对生产、生活产生严重影响的配电室等,也属于特殊重要设备室

数据中心设计规范 GB50174-2017第13.1.2条规定:

A级数据中心的主机房宜设置气体灭火系统,也可设置细水雾灭火系统。当A级数据中心内的电子信息系统在其他数据中心内安装有承担相同功能的备份系统时,也可设置自动喷水灭火系统

数据中心设计规范 GB50174-2017第13.1.3条规定:

B级数据中心和C级数据中心的主机房宜设置气体灭火系统,也可设置细水雾灭火系统或自动喷水灭火系统

数据中心设计规范 GB50174-2017第13.1.4条规定:

总控中心等长期有人工作的区域应设置自动喷水灭火系统

上述为根据国家规范的个人理解,有些地区技术文明可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑