配电房的发电机室及储油室门口需不需要安装人体静电释放装置

配电房的发电机室及储油室门口需不需要安装人体静电释放装置

maya | 2022-04-26 09:31
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

周家斌 2022-05-08 23:35 00 [回复]举报

一、《民用建筑电气设计标准》 GB51348-2019,6.1.12 柴油发电机房接地与通信应符合下列规定:     1 机房内的接地,宜采用共用接地;     2 燃油系统的设备与管道应采取防静电接地措施

二、《电力设备典型消防规程》 DL5027-2015、8.3.1 发电厂内应划定油区,油区四周应设置1.8m高的围栅,并挂有“严禁烟火”等明显的警告标示牌。当利用厂区围墙作为油区的围墙时,该段厂区围墙应为2.5m高的实体围墙。油区应设置人体静电释放器。 8.3.2 油区必须制订油区出入制度,进入油区人员应交出火种,关闭随身携带的无线通信设施,去除身体静电,不准穿钉有铁掌的鞋和容易产生静电火花的化纤服装进入油区。非值班人员进入油区应进行登记。

   虽然发电机室及储油室都是柴油,闪点不小于60°,但是门口建议要安装人体静电释放装置