湿式报警阀前安装减压阀,那么减压阀前还用安装旁通吗

有这个要求吗。感谢

勤务员 | 2025-05-05 10:19
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

牛丫头消防课堂 2025-05-05 16:05 00 [回复]举报

依据《自动喷水灭火系统设计规范》第9.3.5 条,当连接两个及以上报警阀组时,应设置备用减压阀。减压阀前后应设控制阀和压力表。

已经设置备用减压阀,并且前后设置阀门,只要关闭前后阀门,就可以检修、更换减压阀组件,此时备用减压阀工作,不影响管网的压力。


周家斌 2025-05-06 08:49 00 [回复]举报

有备用减压阀组了,做到了安全备份和冗余,可以正常维修(护)其中的阀组,无必要再做旁通管路。

李勤 2025-05-07 13:20 00 [回复]举报