消防问答 > 自喷灭火系统 提问

湿式报警阀组上下腔压力

自动喷水灭火系统施工及验收规范GB50216-2017-9维护管理表9.0.6湿式报警阀主阀锈蚀状况,各个部件连接处无泄漏现象。主阀前后压力表读数准确及两表压差符合要求(<0.01Mpa). 提问湿式报警阀组上下腔压力是否<0.01Mpa为符合要求?个人认为该规范是错误的,湿式报警阀组上下腔压力应不小于0.01Mpa,湿式报警阀组才能保持正常工作状态。谢谢!

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 3 回答

EHS专家-DL 25-05-12

根据规范第9.0.6条,‌湿式报警阀系统侧(上腔)与供水侧(下腔)压力差应<0.01MPa‌,该要求针对的是维护检测时的压力状态,而非正常工况下的运行阈值。在非火灾情况下,上腔(系统侧)压力需略高于下腔(供水侧)压力,使阀瓣保持关闭,有压水对上下腔有效接触面积不同,上腔要大于下腔,所以计算两者压强相差不大,乘以接触面积后压力上腔还是大于下腔的,可以压的住。

0 0 [回复]举报

Along Niusk 25-05-13

首先,纠正一下,国标名为:自动喷水灭火系统施工及验收规范 GB50261-2017

其次,原文写的是上下腔的“压力表 差”——压力表读数差

一方面要允许偏差是因为要考虑机械式压力表的精准度可能导致读数偏差

另一方面,要考虑湿式阀组的动作机理:当上腔压力严重大于下腔时,可能给水系统故障/表故障/补偿器故障等,应排查检修。当上腔压力严重小于下腔时,就更不科学了,可能同时出现给水系统故障和阀组隔瓣卡阻,或者压力表故障,也应排查检修。

总之,阀组上下腔压力差值是一个判定基准,不是一个绝对值

0 0 [回复]举报

牛丫头消防课堂 25-05-15

这个问题,你明白原理就不纠结了。上下腔压差太大时,会导致打开报警阀的时间较长,报警阀打不开,压力开关没法动作,启动消防水泵的时间就会受到影响,影响火灾扑救。

0 0 [回复]举报

最新问题

关闭

关闭