消防问答 > 自喷灭火系统 提问

对于一些安装距离不足的场所可不可以加集热罩作为辅助装置,集热罩(挡水板)它的作用是集热作用大还是挡水作用大呢?

对于一些安装距离不足的场所可不可以加集热罩作为辅助装置,集热罩(挡水板)它的作用是集热作用大还是挡水作用大呢?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 4 回答

资源网小助理 25-02-10



集热罩”的由来:集热挡水板


《自动喷水灭火系统设计规范》GB 50084-2001(2005年版)


7.1.7 货架内喷头上方的货架层板,应为封闭层板。货架内喷头上方如有孔洞、缝隙,应在喷头的上方设置集热挡水板。集热挡水板应为正方形或圆形金属板,其平面面积不宜小于0.12㎡,周围弯边的下沿,宜与喷头的溅水盘平齐。


7.2.3 当梁、通风管道、成排布置的管道、桥架等障碍物的宽度大于1.2m时,其下方应增设喷头(见图7.2.3)。增设喷头的上方如有缝隙时应设集热板



     该名词给部分工程技术人员造成了困惑,认为集热挡水板可以用来给喷头集热,导致有些场所出现了喷头悬空布置的情况。如下图:



        其实在规范中就限制了“集热罩”的使用,只用于喷头上方有空隙时,防止上部的喷头动作后淋湿下方的喷头而影响喷头动作。


名称的变化:”集热挡水板“→“挡水板:


自动喷水灭火系统设计规范 GB50084-2017


7.1.10 挡水板应为正方形或圆形金属板,其平面面积不宜小于0.12㎡,周围弯边的下沿宜与洒水喷头的溅水盘平齐。除下列情况和相关规范另有规定外,其他场所或部位不应采用挡水板:  

   

1 设置货架内置洒水喷头的仓库,当货架内置洒水喷头上方有孔洞、缝隙时,可在洒水喷头的上方设置挡水板;       


2 宽度大于本规范第7.2.3条规定的障碍物,增设的洒水喷头上方有孔洞、 缝隙时,可在洒水喷头的上方设置挡水板。


       

      在2017版的自动喷水灭火系统设计规范中,对该名词进行了修改(挡水板),同时在条文说明中也进行了解释:喷头动作所需的热量主要来自热对流,需要热的烟气流经喷头才能实现。调研中发现,有的商场、超市等采用增设挡水板的方式使喷头悬空布置,喷头与顶板的距离过大,这种布置方式使得喷头的动作大大滞后。美国消防协会标准《自动喷水灭火系统安装标准》NFPA 13也规定,不应采用挡水板作为辅助喷头启动的方式


        所以,“集热罩”不集热。

1 0 [回复]举报

黑面   回复: 资源网小助理25-07-10

学习了

0 0 [回复]举报

潘天坤 25-02-10

目前名称为挡水板,可能挡水作用大一些(防止上喷头淋湿下喷头的热敏原件)

上述言论为根据国家规范的个人理解和交流探讨,不一定正确,也不能作为依据
有些地区技术文件可能有特别规定,建议楼主多与区域内设计、审查及验收等专家交流,具体以他们意见为准


0 0 [回复]举报

徐海金 25-02-11

没效果,挡水板不能做为集热措施

0 0 [回复]举报

最新问题

关闭

关闭