设在屋顶的稳压泵房,消防电梯机房是否要设防火门?依据规范哪条?

设在屋顶的稳压泵房,消防电梯机房是否要设防火门?依据规范哪条?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 3 回答

南明离火 24-04-30

直接对外的 都可以不设防火门

0 0 [回复]举报

慧亮 24-04-30

对于这些设备用房,规范只规定了开向建筑内的门需要甲级门或乙级门。据体可查看建规GB50016-2014的6.2.7条和消水规GB50974-2014的5.5.12.3条。建筑防火通用规范也只对设置在建内的设备用房作了规定。所以个人理解这些外部的设备用房可以自愿安装防火门。

0 0 [回复]举报

gx祥子 24-05-06

这个设置在屋面的设备间,也有受火灾的威胁可能,应该设置防火门。

0 0 [回复]举报