疏散指示标志灯吊装吊链长度有要求不么?

在楼层较高的空间,疏散指示标志灯采用金属吊链吊装,这个吊链有长度要求么?连接灯具线软管有长度要求么?


请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 3 回答

罗马苏丹 25-06-19

从接线盒、管路、槽盒等处引到系统部件的线路,当采用可弯曲金属电气导管保护时,其长度不应大于 2m。

可以参考这个,但也不能低于车库净高要求,别妨碍车辆人员通行

2 0 [回复]举报

牛丫头消防课堂 25-06-19

第一,规范对于吊杆长度没有要求;

第二,金属软管有长度限定,不超过2m。我说的是金属保护管长度。

安装在疏散走道、通道上方时:    

  1)室内高度不大于3.5m的场所,标志灯底边距地面的高度宜为2.2m~2.5m;       

2)室内高度大于3.5m的场所,特大型、大型、中型标志灯底边距地面高度不宜小于3m,且不宜大于6m。


4.3.15 从接线盒、管路、槽盒等处引到系统部件的线路,当采用可弯曲金属电气导管保护时,其长度不应大于2m,且金属导管应入盒并固定。

1 0 [回复]举报

李勤 25-06-20

1 0 [回复]举报