消防问答 > 火灾自动报警 提问

小区临街的商业服务网点的消防设施设置要求

请问各位老师,小区临街的商业服务网点必须设置自动喷水灭火系统和火灾探测器吗?

请写下您的回答回答

הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


共 6 回答

潘天坤 25-05-14

请问建筑面积是多少平方米?

0 0 [回复]举报

看猫走不动道   回复: 潘天坤25-05-15

不固定,二三十到两百多的都有。

0 0 [回复]举报

wetom 25-05-15

个人理解,住宅底部的商业服务网点火灾报警应设置,自喷不设。

1 0 [回复]举报

大恒 25-05-15

8.1.9 除建筑内的游泳池、浴池、溜冰场可不设置自动灭火系统外,下列民用建筑、场所和平时使用的人民防空工程应设置自动灭火系统:

5 任一层建筑面积大于1500㎡或总建筑面积大于3000㎡的单、多层展览建筑、商店建筑、餐饮建筑和旅馆建筑;

底商大于1500的 或者两层整体超3000的  还是要设置啊

1 0 [回复]举报

牛丫头消防课堂 25-05-15

依据《建筑防火通用规范》第8.3.2条及其条文说明,建筑面积超过100平米的商店应设置火灾自动报警系统,所以商业服务网点应设置火灾自动报警系统。

至于是否设置喷淋,看面积,如果一层面积超过1500平米,可参照第8.1.9条设置自动喷水灭火系统。工程中多数都设置了喷淋。

供你参考

1 0 [回复]举报

看猫走不动道   回复: 牛丫头消防课堂25-05-16

谢谢老师,我抖音有关注你。

1 0 [回复]举报

最新问题

关闭

关闭